# AccessControlEntriesPerFabric = 4?

**URL:** <https://community.inovelli.com/t/accesscontrolentriesperfabric-4/20090>\
**Category:** Product Support\
**Tags:** 4-way, white-series, north-america\
**Created:** [September 30, 2025, 12:05am UTC](https://community.inovelli.com/t/accesscontrolentriesperfabric-4/20090 "2025-09-30T00:05:58Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![harryh](https://community.inovelli.com/user_avatar/community.inovelli.com/harryh/32/15179_2.png) [@harryh](https://community.inovelli.com/u/harryh)\
**Post date:** [September 30, 2025, 12:05am UTC](https://community.inovelli.com/t/accesscontrolentriesperfabric-4/20090/1 "2025-09-30T00:05:58Z")

</div>

Is there any particular reason that the white switches have AccessControlEntriesPerFabric = 4?

If I’m understanding this correctly, this makes it impossible to use matter binding in a 4 way switch configuration. Each switch needs to accept 5 bindings (2 from each other switch in the group + the original ACL entry).

Seems like kind of a problem. Can this be changed?

---

<div class="post-metadata">

**Author:** ![harryh](https://community.inovelli.com/user_avatar/community.inovelli.com/harryh/32/15179_2.png) [@harryh](https://community.inovelli.com/u/harryh)\
**Post date:** [September 30, 2025, 12:23am UTC](https://community.inovelli.com/t/accesscontrolentriesperfabric-4/20090/3 "2025-09-30T00:23:31Z")

</div>

Oh wait, nevermind. I can just do a single binding entry to the whole endpoint, I don’t need 2 separate binds to cluster 6 (OnOff) and 8 (LevelControl). I think I’m good. Yay.

---

<div class="post-metadata">

**Author:** ![andrewk](https://community.inovelli.com/user_avatar/community.inovelli.com/andrewk/32/18803_2.png) [@andrewk](https://community.inovelli.com/u/andrewk)\
**Post date:** [October 1, 2025, 2:36pm UTC](https://community.inovelli.com/t/accesscontrolentriesperfabric-4/20090/4 "2025-10-01T14:36:33Z")

</div>

Harry,

I assume you still need an automation to handle the case when a switch is turned on or off via HA or the like? The last time I looked at this Matter bindings only “bound” to the actual switch paddle.

---

<div class="post-metadata">

**Author:** ![harryh](https://community.inovelli.com/user_avatar/community.inovelli.com/harryh/32/15179_2.png) [@harryh](https://community.inovelli.com/u/harryh)\
**Post date:** [October 1, 2025, 3:01pm UTC](https://community.inovelli.com/t/accesscontrolentriesperfabric-4/20090/5 "2025-10-01T15:01:09Z")

</div>

Ya, this aspect of matter bindings is pretty annoying. The way I have currently decided to deal with this is by creating a light group consisting off all the switches in a 3-way (or 4-way) setup and then only having that group in the UI that I use.

---

<div class="post-metadata">

**Author:** ![system](https://community.inovelli.com/uploads/default/original/2X/3/3ce99ae1731871236d0a530943eca38884dd895f.png) [@system](https://community.inovelli.com/u/system)\
**Post date:** [December 8, 2025, 3:01am UTC](https://community.inovelli.com/t/accesscontrolentriesperfabric-4/20090/6 "2025-12-08T03:01:36Z")

</div>

Closed on December 8, 2025, 3:01am UTC

This topic was automatically closed 67 days after the last reply. New replies are no longer allowed.