Vera 3-Way Configuration

I have two Gen 2 dimmers (one red and one black) that are not working in a 3-way / 4-Way capacity on Vera. They both have constant power and work when the dumb switches are in the right configuration, but do not seem to respond whenever a dumb switch is turned off, and the switch still “thinks” it is on. Is there a configuration that needs to be updated on the switch so that it “knows” that it is in a 3/4 way environment?

All of the single poles work great!

Yes. You will want to set the AC Power Type (Neutral vs Non-Neutral) and Switch Type (Load Only vs 3 Way).

Page 9 in the manual (Red: https://inovelli.com/wp-content/uploads/LZW31-SN/LZW31-SN-Dimmer-Manual.pdf) talks about the settings (21 & 22).