Looking for any ideas here, still actively troubleshooting this issue.
I have a circuit with a switch and 3 outlets. With a standard switch I am getting 120v on, 0v off as expected. Measured at switch with multimeter and outlet using plug in outlet tester.
Install a Red On\Off switch and I measure 120v on at outlet and 30v when off at the outlet. At the switch, I am measuring 0v when off (load to ground, load to neutral, neutral to ground - all 0v).
I have heard that the plug in testers can read 30v due to very low amp bleed onto the lines, but this is enough current to dimly light a couple of strings of outdoor led lights. If it is bleed, I wouldn’t expect enough current to light up the lights. LED’s do not light up with a traditional switch.
I have tried two different red switches, both with the same results.
Anyone have any ideas what could be going on? Any other tests to try?
Thanks for any guidance you can offer.
Edit: Adding details to make it easier for anyone new to the thread. These are the ultimately relevant details. Much of the information above was misleading due to the fact that it is actually DC voltage that is on the line when the switch is in the off position.
Root issue: My switch is passing 50v DC onto the line when in the off position.
My confusion throughout stemmed from the fact that I was measuring DC using the AC setting on my meter (I had no idea would actually work). Turns out that my non-RMS meter will read DC voltage on the AC setting, but only in one direction. Unlike AC, if the polarity is reversed DC gives a reading of 0 so I would see inconsistent readings depending on how I was hooking up the leads.
Some key points to clarify based on some comments on the thread:
- This is a 2nd Gen Red SWITCH (not dimmer) - LZW30-SN
- This is in a single pole configuration (not a 3-way configuration)
- Pulling the air gap does resolve the issue, as does shutting down the circuit at the breaker