Borrowing a neutral from same circuit
I’m trying to install a VZM31-SN Blue dimmer switch in a 3-Way configuration.
I have a wiring setup where the line comes into one box without any neutral, goes through travelers to another switch box that contains no line, but the load and other neutrals on the same circuit.
It looks something like this:
I found a wiring diagram on here that should work that doesn’t involve using any neutrals:
Can I use a neutral on the same circuit and connect it to the dimmer switch’s neutral connection? Will that provide any benefit, as in possibly not needing a bypass? Is there a better way to wire the circuit?
What type of wiring do you have? Knob and tube or individual conductors like THHN in EMT (conduit)?
The drawing that you posted is slightly different from your topology, but the concept is the same.
For a non-neutral solution:
LEFT BOX: Put the Aux in the left box and connect the incoming hot to the Neutral terminal. (Aux needs a hot on the Neutral terminal with a non-neutral.) Connect the red going to the other box to the other Neutral back-wire hole. This will send a hot to the right box. Cap off the white.
RIGHT BOX: Inovelli goes here. Black to Load. Red to Line. Cap off the white.
That should give you a 3-way w/Aux non-neutral. As always, you may need a bypass at the light, depending on the load.
Regarding using a neutral from the same branch circuit i.e. breaker. If it’s the same branch circuit, it’s not technically considered to be a borrowed neutral, so that wouldn’t be prohibited by code. That may work in your situation.
I don’t recommend or instruct using an available same circuit/different leg neutral, only because some have tried it on their own in the past and received mixed results. But who knows what they really did . . if you get my point.
If you do try the Neutral, remember that the Aux gets a neutral, not a hot, in that configuration.
Thank you for your help. I’ll give it a try without the neutral first and see if I’ll need the bypass.
What do you mean that if I use a neutral, the Aux gets a neutral too?
In a neutral configuration, the Aux has a neutral attached to the neutral terminal. In a non-neutral configuration, the Aux has a hot attached to the neutral terminal. So in a neutral config, there must be a neutral conductor attached to the Neutral terminal, as opposed to a hot conductor for a non-neutral configuration. Refer to the wiring diagrams for neutral and non-neutral to see what I’m describing.
This is what I ended up doing. Instead of a non-neutral setup with an AUX switch, I brought a neutral over with a traveler wire to power another dimmer switch on the side with the line. Then I passed the line through the other traveler to the load dimmer. Then I used zigbee bindings to connect the two switches together virtually. This is the wiring setup i did to accomplish that.