[HOW-TO] LZW31-SN Red Series Dimmer Switch Setup | SmartThings
UPDATE: We’ve included instructions for the New App here: Knowledge Base Redirect – Inovelli
Note: This is a work in progress – I at least wanted to get the initial setup videos up
Hey everyone – I wanted to provide a centralized location that explains how to properly setup your LZW31-SN (Red Series) switches. This thread will be broken down into the following segments:
  1. Preparing Your Setup (Neutral, Non-Neutral & Limitations)
  2. Wiring Help (Getting Started, Guides, etc)
  3. Setting up a Multi-Switch (3-Way, 4-Way, etc)
  4. SmartThings Setup
  5. FAQ’s
1. Preparing Your Setup (Neutral/Non-Neutral & Limitations)
First, you’ll need to understand whether or not you have a neutral wire inside your gang-box. Here’s a video that actually is pretty helpful (shoutout to Leviton):
This switch can be used either with or without a neutral wire. However, if you do have a neutral, we strongly advise you use it as there are some trade-offs in performance if you install this switch without a neutral.
If you DO NOT HAVE A NEUTRAL here are the limitations:
  • Bypass: You will need to install a bypass if your total load is below 25W
  • Energy Monitoring: You will not be able to use the energy monitoring function
  • 3-Way or Multi-Switch Installation: You can only install this switch in a multi-switch setup with an auxiliary switch such as GE’s or HomeSeer’s and you will not be able to use another smart switch or dumb (existing) switch.
Once you’ve identified whether or not you have a neutral wire, it’s time to figure out what setup you have (Single-Pole, Multi-Switch Setup).
Single-Pole Setup = 1 Switch controls a Load
Multi-Switch Setup = More than one switch controls a Load
  • 3-Way Switch = 2 Switches controls a Load
  • 4-Way Switch = 3 Switches controls a Load
  • 5-Way Switch = 4 Switches controls a Load
For Multi-Switch Setups, there are various options you can use for installation depending on if you have a neutral wire or not.
  • Neutral Wire Setup: You can choose to have either a dumb (existing) switch or an auxiliary switch. You can also choose to install another Inovelli smart switch on the other side, but there are some limitations here and we do not recommend it at this time.
  • Non-Neutral Wire Setup: The only option here in a multi-switch setup is to use an auxiliary switch.
Please see FAQ’s below for questions around dumb vs aux switch benefits (in a nutshell, a dumb switch only allows for On/Off at the non-smart switch side, whereas the aux switch provides dimming at the non-smart switch side).
2. Wiring Help
Our official stance on offering help is that we cannot provide specific installation instructions outside of our wiring diagrams as we are not licensed electricians and the liability insurance would be astronomical. That said, there are times when we (along with the community) can provide input that may help. But please know we are not responsible for any damages and please use at your own risk. Our best advice would be to hire an electrician if you’re not sure what you’re doing.
Ok, now that that’s out of the way, let’s walk you through what you’ll need to do to get started.
  • Acquire a Multimeter and/or probe
  • Identify Your Wiring
  • Review the Schematics
Let’s begin:
  • Step 1 - Finding the Line (Hot) Wire: Determine where the line is by using your multimeter or probe. To do this, please follow the video below (the video shows a wall outlet, but the logic is similar).
  • Step 2: Identify the remaining wires by following the schematics below (coming soon)
  • Step 3: Wire up your switch (make sure power is off!) and move to Part 3 if you have a Multi-Switch Setup (if not, you can jump to Part 4).
Identifying the Line (Hot) Wire:
Once you’ve decided what scenario you have (ie: Neutral, Non-Neutral / Aux Switch, Dumb Switch, etc) it’s time to program the switch correctly to let the switch know what scenario it’s in.
In other words, the switches internal computer needs to understand that it’s installed in a Neutral or Non-Neutral setup and also whether or not it’s wired up to an Aux Switch or Dumb Switch.
To do this, you need to configure at the switch via the configuration button. Please follow the videos below for help.
Neutral Setup + Dumb Switch
Neutral Setup + Aux Switch
Non-Neutral Setup + Aux Switch
Once the switch is programmed, it should work manually from either side of the multi-switch setup.
Once the switch manually works, it’s time to pair it to SmartThings. There are currently two apps that can be used, which are the Classic App (Android | iOS) or the New App (Android | iOS).
As of January 23, 2020, we still recommend the Classic App as it provides more functionality for our switches, however, we’ve also confirmed that the new app does provide some of the advanced features, so we’ll include directions for both.
There are 5 Steps:
  1. Pairing to SmartThings
  2. Installing the Device Handlers
  3. Understanding the Device Handler Settings
  4. Setting up Notifications
  5. Setting up Scenes
SmartThings Classic Setup
  • Restore power to your switch and if wired properly, the LED bar will light up (should flash a series of colors, then turn blue)
  • Open up your SmartThings Classic app and click on the, “My Home” tab followed by the, “Things” tab
  • Scroll to the bottom and click on, “Add a Thing” or click on the (+) at the top right of the screen
  • Press the config button (A) 3x and the LED bar should flash blue (if it doesn’t, try pressing the buttons faster or slower) indicating the switch is in inclusion mode. If successful, the switch LED Bar (B) will turn Green. If unsuccessful, the LED Bar will turn RED.
  • You should now see that your device is detected (it should say, “Z-Wave Dimmer Switch” or something similar)
  • After your device is detected, press, “Save” (or if you’d like to rename your device, please do so and click, “Save”)
  • Once you click, “Save” a pop-up will appear asking you to, “Confirm Paired Devices” — Click, “OK”
  • Now, you should be back at the, “My Home” screen and you should be able to see your switch!
  • Z-Wave Range Check: Easily check whether or not your switch is within range by holding the Config Button (A) for 5-10 seconds. The LED bar will indicate: RED = Not in Range, or = Within Range GREEN (Good Signal).
Final Thoughts / Tips: If you’re having issues pairing your switch, there’s a couple things you can try. The first one is to hold down the config button for 5 seconds until the LED bar indicates RED or GREEN, where RED = Not in Range, or = Within Range GREEN (Good Signal). If the signal is GREEN, then let’s try an exclusion to reset your switch. Please see below.
SmartThings Exclusion Steps:
  • In the SmartThings Classic App, please click on the menu button
  • Then click, “Hub is Online”
  • Next, click on, “Z-Wave Utilities”
  • Followed by, “General Device Exclusion”
  • Press, “Remove” and tap the Config button 3x (should pulse BLUE)
  • The LED bar should flash GREEN if successful
In order to take advantage of Notifications and Scene Control, you will have to install two Device Handlers as SmartThings does not have these capabilities built in natively.
Open up IDE on your Computer/Tablet:
  • Go to: graph.api.smartthings.com (it’s free)
    • Login using the same Username/Password as your SmartThings Phone App
  • Click on the green, “Login” button on the top right of the screen and login using the same credentials as your SmartThings Phone App
  • Once logged in, click, “My Locations” (top left of the screen) — you should see your HUB’s location there
  • Click on your HUB’s location underneath where it says, “Name”
    • You may be prompted to login again — if so, please do
Now We’re Going to Install the LZW31-SN Device Handler
  • While still in IDE, click on, “My Device Handlers” located at the top/middle of your screen
  • Click the green button labeled, “Create New Device Handler”
  • Then click, “From Code”
  • Copy the code from the following URL: Inovelli Red Series Dimmer Switch DTH
  • After the code is copied (above), paste it in the, “From Code” section (white space)
  • Then click, “Create”
  • Next click, “Publish”
  • Finally, click, “For Me”
Finally, Now That the Device Handler is Installed, We Need to Apply it to the Switch
  • While still in IDE, click on, “My Devices”
  • Find your Inovelli Switch and click on it
  • Scroll to the bottom and click, “Edit”
  • Locate the drop-down menu titled, “Type” and click on it to see a list of device handlers
  • Find the handler we just installed which is called, “Inovelli Dimmer Switch Red Series” (it will probably be at the bottom) and select it
  • Finally, click, “Update” and you should be all set!
To confirm you have the handler installed, please open your SmartThings app, locate your Inovelli switch and click on it. You should see the following:
Now We’re Going to Install the Second Device Handler
  • Copy the code from the following URL: Inovelli Switch Child Device DTH
  • Then click, “Create” (No need to Publish this one)
3. Understanding Device Handler Settings
Now let’s get to know the various settings built into the device handler. It’s a pretty powerful switch! After you’ve selected the switch on the, “My Home” menu, click on the gear icon at the top right (circled in red) of the screen to access the settings:
Let’s go through each of the settings one by one. Default settings are highlighted in Red .
Dimming Speed: How fast or slow the light turns on when you remotely dim the switch
Dimming Speed (From Switch): How fast or slow the light turns on when you manually hold the switch up or down
Ramp Rate: How fast or slow the light turns on/off when you remotely turn on or off the light
Ramp Rate (From Switch): How fast or slow the light turns on/off when you turn on or off the light manually
Minimum Level: The minimum level that the switch can be set at (ie: this is great if your bulb flickers at 10% — you can set the minimum level to be 11% to avoid flickering)
Maximum Level: The maximum level that the switch can be set at
Invert Switch: Honestly, I’m not sure why you’d want to use this, but we threw it in there for fun. Mess with your spouse, friends, etc.
  • Yes = Inverts switch (Up = Off, Down = On)
  • No = Does not invert switch
Auto Off Timer: This will shut off the switch after a certain amount of time.
  • 0 = Disabled
  • 1 – 32,767 Seconds = Enter in a value from 1 – 32,767 seconds
Default Level (Local): This is the default level you can have your switch turn on when you press the paddle on
Default Level (Z-Wave): This is the default level you can have your switch turn on when you turn the switch on remotely
State After Power Restored: If there is a power outage, you can select what you’d like your switch to default to when the power is restored.
  • Previous = Switch returns to the previous state (ie: if the switch was off, it will return off)
  • On = Switch will turn on (even if it was off prior) to a certain level
  • Off = Switch will turn off (even if it was on prior)
LED Strip Color: Change the color of the LED Strip (bottom right of the switch)
  • Choose from the default values which are: Red, Orange, Yellow, Green, Cyan, Blue , Violet, and Pink
LED Strip Intensity: Change the intensity level of the LED Strip (when switch load is turned on)
  • NOTE: By default the LED Strip turns on when the load is turned on. If you’d like the LED Strip to be off when the load is on, set the intensity to 0%
LED Strip Intensity (When Switch is Off): Change the intensity level of the LED Strip (when switch load is turned off)
  • NOTE: By default the LED Strip turns off when the load is turned off. If you’d like the LED Strip to be on when the load is off, set the intensity to anything above 0%.
Active Power Reports: A power level report will be sent based on a percentage level over the last report. For example, if you want a report sent when new power consumption is x% higher than the last report.
Periodic Power & Energy Reports: Choose a time period between when reports of energy and power are sent. Default is 6 minutes, but you can choose anywhere from 1 – 32767 seconds (NOTE: the more reports, the more congested your network can become).
Energy Reports: An energy level report will be sent based on a percentage level over the last report. For example, if you want a report sent when new energy consumption is x% higher than the last report.
AC Power Type: Select whether your house is wired with or without a neutral (by default, the switch is programmed to assume you have a neutral wire)
Switch Type: Select what type of secondary switch (non-smart) you’re using in your 3-Way (or multi-switch) setup.
  • Load Only = This is the default and it assumes your switch is wired in a single-pole setting
  • 3-Way Toggle = This is if you’re using a dumb switch
  • 3-Way Momentary = This is if you’re using an auxiliary (or add-on) switch by GE or HomeSeer
Notifications: This is where you’ll set the notification type (color, intensity, duration, and animation). PLEASE NOTE: You must install the Child Switch Handler in Step 2 for this to work properly.
  • Effect Color: Choose from the default colors
  • Effect Level: This is the intensity (ie: how bright) the notification will be
  • Effect Duration: How long you’d like the notification to last (double-tap to clear it)
  • Effect Type: Here’s where you can choose what animation you’d like the notification to have
With notifications, the sky’s the limit in what you can do. In this example, I’m going to set up a notification that alerts me when a door is unlocked between the hours of 10pm and 8am.
REMEMBER: you need to install both device handlers in Step 2 (above dropdown menu) for this to work.
SELECTING YOUR NOTIFICATION
  • From the, “My Home” tab, click on your Inovelli switch
  • Then, click on the gear icon at the top right of the screen to access the settings for the switch
  • Scroll to the bottom where it says, “LED Notifications”
  • Select your desired effect, level, duration and effect type under, “Notification 1”
  • Click, “Save”
  • If you’ve installed the Child Switch Handler properly, you will now see, “Notification 1” on the screen as highlighted below — turn it on to see how it looks on the switch
  • Once you’re satisfied with the way the notification looks, we’ll setup the actual notification
SETTING UP THE NOTIFICATION
  • Go back to the, “My Home” tab where all your devices show up and click on, “Marketplace”
  • Then, click on, “SmartApps”, followed by, “SmartThings Recommends”
  • Finally, click on, “Smart Lights”
  • Under, “Which devices do you want to control”, we’ll search for the Child Device we just created (it will be called, “WHATEVER YOU NAMED YOUR SWITCH – Notification 1”) — in my case, since I named the switch, “Inovelli Switch – Red Series”, the Child Device will be called, “Inovelli Switch – Red Series (Notification 1)”.
  • Click on the Child Device and click, “Done”
  • Under, “What do you want to do”, select, “Turn On” (this will turn the notification on when triggered)
  • Click on, “Select Trigger” and since I want to have the notification go off when my door unlocks, I’m going to select, “Lock”
  • Click on, “Which Locks” and select your lock
  • Next, click on, “Turn on when” and select, “Unlocked”
  • Finally, since I only wanted to be notified during certain times, I’m going to select, “Only during a certain time” and select the times
  • Click, “Save” and you’re done!
With the device handlers installed, let’s set up some scenes! Before we do so, let’s go over a few basics so you can understand the logic behind how to properly map your scenes.
The way SmartThings works is that it recognizes this switch as a button controller and each button can be broken down into two separate buttons (scenes).
This switch is broken down as follows:
  • The paddle has 5 buttons (Buttons 1-5)
  • The config / favorites button is also considered a button (Button 6)
Buttons 1-5 are split into two scenes (Pushed and Held). Those words have no meaning in that you’re not pushing or holding — it’s just what they’re called.
IMPORTANT: Always remember that when you tap UP, it equals PUSHED and when you tap DOWN = HELD.
Here’s the correct mapping for reference:
  • Tap UP 1x = Button 1 PUSHED
  • Tap DOWN 1x = Button 1 HELD
  • Tap UP 2x = Button 2 PUSHED
  • Tap DOWN 2x = Button 2 HELD
  • Tap UP 3x = Button 3 PUSHED
  • Tap DOWN 3x = Button 3 HELD
  • Tap UP 4x = Button 4 PUSHED
  • Tap DOWN 4x = Button 4 HELD
  • Tap UP 5x = Button 5 PUSHED
  • Tap DOWN 5x = Button 5 HELD
  • Tap the Config/Favorite Button 1x = Button 6 PUSHED
Now that we have a background, let’s configure our first scene. In this example, I’d like to turn off all lights in the house via a double tap down.
  • From the, “My Home” screen, click on, “Marketplace” and then, “SmartApps”
  • Then click on, “SmartThings Recommends”
  • Next, click, “Smart Lights”
  • Click on, “Which devices do you want to control?” and select all the lights you want to turn off and click, “Done”
  • Next, click on, “What do you want to do?” and select, “Turn Off”
  • Next, click on, “Select Trigger” and select, “Button”
  • Click on, “Which Button?” and select the Inovelli Red Series Switch you just installed
  • Where it says, “Button Number” since I want the scene to execute when I DOUBLE TAP down, I would select, “Button Number” and select, “Two”
  • Again, since it’s a double tap DOWN , I would select, “Button Action” and select, “ HELD ” (if it was double tap UP, you’d select PUSHED)
  • Deselect, “Toggle on & off” (unless you want to turn all your lights on from the same button tap sequence)
  • If you’d like this button to only execute during certain times, you can click the, “More Options” and put your times in — otherwise, just click, “Next” and, “Save”
That’s it! If you want a more advanced option, consider downloading and installing the ABC SmartApp, which gives you the ability to lock doors and many other options.
Thanks for the videos. This helps a lot. A lot of people are move visual. This helps clear up a lot of confusion.
Yeah for sure! @Brianna_Inovelli and I plan on knocking out videos for all parameters over the next few weeks.
In addition, the vision here is to have a collective space where as many Hub instructions are. Or maybe I’ll have a separate thread for each Hub. Not sure yet!
I think a separate thread for each hub is better. It’ll be much cleaner and clearer to follow.
I think you’re right. Then we can actually direct ppl here from the manuals too and the information will likely be as up to date as possible as more people can chime in!
My thought is exactly that.
Like @Eric_Inovelli said, we’ll be making more videos here soon so if you have any suggestions for topics throw them below! :slight_smile:
Does the LZW31-SN work on the newer SmartThings 3 hub yet? I successfully installed the red series LZW31-SN dimming switch, and paired it with the SmartThings v3 hub, but only could do it using a generic type “Z-Wave Metering Dimmer”. I can turn the lighs on and off, and dim.
I followed the great instructions and created a device handler by pasting in this code from https://raw.githubusercontent.com/InovelliUSA/SmartThingsInovelli/master/devicetypes/inovelliusa/inovelli-dimmer-red-series-lzw31-sn.src/inovelli-dimmer-red-series-lzw31-sn.groovy, but I cannot the handler type when I edit the LZW31-SN device. The only item I can find is “Inovelli 2-Channel Smart Plug”. Is this futile or maybe I am missing something?
Mine is working fine with the V3 hub and new app. Check a couple things:
  1. make sure the DTH is published
  2. scroll all the way to the bottom of the Type list. Custom DTH’s are listed at the very bottom.
I did swap the VID with generic-dimmer-power-energy so i could see the power and energy charts in the new app. I believe power monitoring only works for neutral wire installations, so i’m not sure if @EricM_Inovelli would want to use this VID in the DTH instead of the current one, or if its possible to somehow make the VID variable based on the config setting for neutral wire. Although the power and energy tiles may stay hidden if they are never reported. Someone would have to test.
Forgot to update the vids for power & energy support in the new app. Thanks for the reminder.
no problem. btw your latest update to set child devices to isComponent: false is much more friendly for the new app, too. However, there is currently a bug on SmartThings side where the device tile doesn’t accurately display the switch state of the child device. Just an FYI in case anyone brings it up.
Thanks for the detailed instructions!
This is my first attempt configuring a smart switch and after a lot of videos and reading I thought I was able to wire everything up.
I have a neutral wire with a dumb switch (a legrand toggle switch).
After configuring the inovelli lzw31-sn red series, I’m able to turn on and off the lights, but only if the dumb switch is in a certain position.
I wonder what I must have done wrong and if someone could give me any guidance on how to solve that.
Did you set parameter 22 to 1 (Multi-Dumb switch)?
Hi Bry, thanks for helping out!
I thought I did but after your reply I tried again and now it’s working!
And I believe I know what I was doing wrong. I was being too slow to press 13 times to access the parameter 22. Rewatching the videos I’ve noticed the person was pressing the button way faster than I was.
So I’ve tried faster and it’s now working as expected!
Thank you so much for your help!!
@thiagomp Thanks. Which videos did you refer to? There is someone else having the same problem?
@Bry, this was the video that made me notice the config button press speed: https://youtu.be/WRIV-6yezrw
I guess I was too worried trying to count the seconds, the color changes etc.
I’m having trouble setting up my first automation. I’ve installed the Handlers, and set up a simple scene pictured here based off of a previously set scene through Alexa which already has all the desired devices controlled. When I press the down paddle 3x, nothing happens. Any suggestions on what I could be missing? All of the “More options” settings are not set to anything. Thanks in advance.
You’re in Smart Lighting, right? Is “Down Button” the name of your Inovelli switch?
After you select “Button” as the trigger, you select your Inovelli switch as “Which Button?”. Then you select the “Button number” and “Button action” based on the number of taps and up or down.
Take a look at the article below, particularly “Understanding Button Mapping”
Great thanks, I’ve straightened that part out, but I’m only seeing the “pushed” and not “held” option. Not the end of the world but I’d rather be turning my house off using the off switch.
That doesn’t look right to me. Your “Button Action” selections should either be “Pushed” or “Held”, corresponding to top or bottom tap.
Are you sure you are using the proper Device Handler? Go into the IDE, open the dimmer’s page, select Edit and insure that Inovelli Dimmer Red Series LZW31-SN is selected.
If that’s ok, go to the IDE’s Device Handler’s section and open the DH for the LZW31-SN and check the date:
  • Author: Eric Maycock (erocm123)
  • Date: 2020-09-21